Gutor SDC Specifications
Typical single-line drawing
Battery voltage and UPS ratings
Standard configuration
- Single system
- Rectifier input voltage — 3 x 400 V + 10/-10
- Rectifier input frequency — 50 Hz +/- 8%
- Ripple filter — ≤2% rms with parallel battery
- Six-pulse rectifier with isolation transformer
- Rectifier input switch
- Fixed charging voltage IU characteristic
- System front panel w. mimic and add. LEDs for direct alarm display
- LCD display unit with keyboard
- External connection board:
- Common alarm 2 x NO/NC
- Charger failure NO/NC
- Remote ON/OFF
- Emergency stop (internal or external power supply)
- Input to activate boost charge
- Input to activate initial charge
- Input to inhibit boost and initial charge
- Connection for battery temperature sensor
- Input for signaling battery fuse/MCCB
- Connection for remote display
- RS-232 Interface (event log download)
- Battery capacity test (full discharge with current load)
- DC ground fault alarm
Standard configuration (continued)
- Bottom cable entry
- Ground terminal
- N+1 monitored two-speed fans (above 100 A)
- Ambient temperature range from -10 to +40 °C
Options
System
- Parallel redundant configuration with load sharing
- DC Distribution
- Earth-fault monitoring
Rectifier
- Other input voltages (190 – 690 V)
- Rectifier input frequency 60 Hz +/-8%
- Rectifier input/output protection (MCCB / isolator)
- 12-pulse rectifier with isolation transformer
- Ripple filter
- Dropping diode
Battery
- Battery circuit protection box (MCCB/Fuse)
- Battery circuit protection in rectifier (MCCB/Fuse)
- Low–voltage disconnect contactor
- Battery management system
- Battery temperature sensor
Indication and alarms
- Charger ON · 4 x programmable
- Boost charge ON · Fan fault
- Line power failure · DC current overload
- DC out of tolerance · Internal PSU fault
- Battery discharged · DC ground fault
- Battery disconnected · Overtemperature
- DC fuse blown
Communication Interfaces
- Front-panel analog meter
- Transducer
- Relay board, 16 failsafe NO/NC contacts
- RJ-45 Ethernet port for Web browser based monitoring
- RS-485 modbus protocol (slave)
- External time synchronization
- IEC 61850
Mechanical
- Top/bottom cable entry
- Protection up to IP52 (NEMA 12)
- Air filters at air inlet
- Ventilation 100% redundant
- Seismic design
- Space heaters
- Panel lighting
- Frame color as required
Additional options are available on request
Human-machine interface (front panel)
The front panel includes a comprehensive and flexible human-machine interface. It is divided into four sections:
- The system panel shows the system’s current state of operation (i.e., which part of the system is currently supplying the load and which is in stand-by mode). LEDs also indicate possible faults.
- Use the operations panel to turn the system on and off. The lamp-test button indicates whether all LED indication lights are functioning properly. To shut down the system, you have to press the ON and OFF buttons at the same time.
- The display unit consists of a liquid crystal display, an alarm LED, an acoustic alarm, and a keypad. From here, the user can set operational parameters, obtain current measurement data, and access the event and alarm logs.
- On the alarm indication panel, the respective LEDs light up to indicate a possible fault or after an alarm has occurred.
Operational parameters
- Selectable second display language
- Auto start
- Charge mode (float/boost/initial)
- Auto boost (charge)
- Battery capacity test
- Advanced battery monitor test (optional)
- Set date/time
Indication and measurements
- Operating mode (float/boost/initial)
- DC total current
- Battery voltage and current
- AC rectifier line power voltage and current
- Battery temperature (with optional sensor)
- Time left in battery operation with current load (option only with advanced battery monitoring)
- Event log with date/time (operating mode changes and alarms)